In looking at the specs for the DLS-90, it can be seen that it may pull as much as 22 amps continuous. I'm conjecturing then that is when it's at its 90 AMP Peak output voltage DC? The data sheet suggests that it will always charge at the highest initially and then 3-step down from there, so you'll need to allow for that.
How big is your bank of batteries? What size generator do you plan on running?
The rated max 22 cont. amps AC is at the limit of the 2000 series of generators that most people seem to prefer. and that does not even allow for other AC loads running on the generator at the same time.
In addition, the AC peak demand (inrush) is up to 40 amps @108v which, at 4320 Watts, is far beyond the peak amperage rating of any 2000w series generator. It's a very short-lived inrush because it's just charging some capacitors, but that is a very big hit on the generator and might trigger the overload protection cut out. I have had this problem before with an inverter generator even though the inrush current was less than the peak output of the generator.
Anyway, even if you step up to a 3000w series generator, you still won't have much excess capacity to run other devices when your batteries are in deep charging mode on a DLS-90. Maybe you could consider getting a smaller unit, unless your battery bank is big and charge time is very important. Hope that helps...